An electrician wants to pull power-limited fire alarm conductors into the same conduit as 120 V lighting branch circuit conductors to save time. What is the correct ruling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1006
- C: Not permitted, since power-limited fire alarm conductors must be separated from power conductors
Explanation
Article 760 requires power-limited fire alarm circuit conductors to be separated from electric light, power, Class 1 and non-power-limited circuit conductors. They may not share a raceway, cable, or enclosure with them except under narrow conditions such as a listed barrier or specific separation within enclosures.