Question 1006 of 297 · NICET Fire Alarm Systems Level III

An electrician wants to pull power-limited fire alarm conductors into the same conduit as 120 V lighting branch circuit conductors to save time. What is the correct ruling?

Exactly one answer is correct.

Show solution

Correct answer to question 1006

  • C: Not permitted, since power-limited fire alarm conductors must be separated from power conductors

Explanation

Article 760 requires power-limited fire alarm circuit conductors to be separated from electric light, power, Class 1 and non-power-limited circuit conductors. They may not share a raceway, cable, or enclosure with them except under narrow conditions such as a listed barrier or specific separation within enclosures.