On a Class A initiating device circuit, the specifications require the outgoing and return conductors to follow separate routes. Where does NFPA 72 permit them to run together in the same cable or raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1009
- C: For up to 10 ft where they enter or leave a device or control unit enclosure
Explanation
Separating the outgoing and return paths is what gives a Class A circuit its ability to survive a single open or damaged cable. NFPA 72 allows a limited exception of 10 ft where conductors enter or exit an initiating device, notification appliance, or control unit enclosure.