Question 1009 of 297 · NICET Fire Alarm Systems Level III

On a Class A initiating device circuit, the specifications require the outgoing and return conductors to follow separate routes. Where does NFPA 72 permit them to run together in the same cable or raceway?

Exactly one answer is correct.

Show solution

Correct answer to question 1009

  • C: For up to 10 ft where they enter or leave a device or control unit enclosure

Explanation

Separating the outgoing and return paths is what gives a Class A circuit its ability to survive a single open or damaged cable. NFPA 72 allows a limited exception of 10 ft where conductors enter or exit an initiating device, notification appliance, or control unit enclosure.