While inspecting rough-in, you see fire alarm cable laid directly on the lay-in ceiling tiles and tied to the ceiling grid wires. What is the correct direction to the installer?

Exactly one answer is correct.

Show solution

Correct answer to question 1004

  • B: Support the cable from the building structure, independent of the ceiling grid and its wires

Explanation

Fire alarm cables must be supported by the building structure so they are not damaged by normal building use. The NEC does not allow ceiling grid support wires or the ceiling grid itself to serve as the means of support unless the support wires are installed and identified for that purpose.