Question 1004 of 297 · NICET Fire Alarm Systems Level III
While inspecting rough-in, you see fire alarm cable laid directly on the lay-in ceiling tiles and tied to the ceiling grid wires. What is the correct direction to the installer?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1004
- B: Support the cable from the building structure, independent of the ceiling grid and its wires
Explanation
Fire alarm cables must be supported by the building structure so they are not damaged by normal building use. The NEC does not allow ceiling grid support wires or the ceiling grid itself to serve as the means of support unless the support wires are installed and identified for that purpose.
More questions: Installation
- 1005Power-limited fire alarm cable must be run without raceway through a ceiling cavity that is used as a return air plenum. Which cable type is required?
- 1006An electrician wants to pull power-limited fire alarm conductors into the same conduit as 120 V lighting branch circuit conductors to save time. What is the correct ruling?
- 1007Your crew has run fire alarm cable through a 2-hour rated corridor wall. What must you confirm before the wall is closed up?
- 1008Which description matches pathway survivability Level 3 in NFPA 72?
- 1009On a Class A initiating device circuit, the specifications require the outgoing and return conductors to follow separate routes. Where does NFPA 72 permit them to run together in the same cable or raceway?
- 1010Which performance does a Class X pathway add compared with a Class A pathway?