The general contractor asks for smoke detectors to be installed now, while drywall sanding is still under way, so the area can be protected. What is the proper approach?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1012
- B: Install only if the AHJ requires it, keep them protected, then clean or replace them before acceptance
Explanation
NFPA 72 generally prohibits installing smoke detectors until construction cleanup is complete. Where they must be installed earlier for protection during construction, they must be protected from contamination and then cleaned or replaced before the system is accepted, since dust shifts sensitivity and causes nuisance alarms.
More questions: Installation
- 1013An addressable relay module will drop out the hold-open power for a smoke damper actuator. Where must the module be located relative to the controlled component?
- 1014During commissioning, the elevator lobby smoke detector on the designated recall level is activated. Where should the elevators go?
- 1015Which detector activations must cause the visual fire warning symbol in the elevator car to flash?
- 1016Heat detectors are being installed to shunt trip the elevator power in a sprinklered machine room. Which installation meets NFPA 72?
- 1017The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?
- 1018A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?