An addressable relay module will drop out the hold-open power for a smoke damper actuator. Where must the module be located relative to the controlled component?

Exactly one answer is correct.

Show solution

Correct answer to question 1013

  • B: Within 3 ft of the controlled component, unless the wiring between them is monitored

Explanation

For emergency control functions, NFPA 72 limits the unmonitored wiring between the fire alarm interface relay and the component it controls. The relay or module must be within 3 ft of the controlled circuit or appliance, or the wiring between them must be monitored for integrity.