Question 1014 of 297 · NICET Fire Alarm Systems Level III
During commissioning, the elevator lobby smoke detector on the designated recall level is activated. Where should the elevators go?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1014
- D: To the alternate recall level
Explanation
Phase I recall normally sends the cars to the designated level. If the initiating device is at the designated level itself, the cars must be recalled to the alternate level so they do not open onto the fire floor. Commissioning must test both outputs.
More questions: Installation
- 1015Which detector activations must cause the visual fire warning symbol in the elevator car to flash?
- 1016Heat detectors are being installed to shunt trip the elevator power in a sprinklered machine room. Which installation meets NFPA 72?
- 1017The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?
- 1018A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?
- 1019What happens to doors held open by fire alarm controlled magnetic door holders when building power fails?
- 1020An access-controlled egress door is electrically locked. What must happen to it when the building fire alarm system activates?