Question 1015 of 297 · NICET Fire Alarm Systems Level III
Which detector activations must cause the visual fire warning symbol in the elevator car to flash?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1015
- C: Machine room, control space, or hoistway detectors
Explanation
The flashing fire hat tells firefighters that the elevator equipment or hoistway may be affected by fire, so it is driven by the machine room, control space, and hoistway detectors through a separate output. Lobby detectors on other floors only cause recall.
More questions: Installation
- 1016Heat detectors are being installed to shunt trip the elevator power in a sprinklered machine room. Which installation meets NFPA 72?
- 1017The sprinkler contractor proposes using the hoistway waterflow switch to initiate elevator shunt trip. The switch has a 60 second retard. What is the correct ruling?
- 1018A duct smoke detector is connected to the building fire alarm system to shut down an air handler. When it activates, what signal does NFPA 72 normally require it to initiate at the control unit?
- 1019What happens to doors held open by fire alarm controlled magnetic door holders when building power fails?
- 1020An access-controlled egress door is electrically locked. What must happen to it when the building fire alarm system activates?
- 1021The fire alarm control unit will be in a storage room that is not continuously occupied. What detection does NFPA 72 require at the control unit location?