Three strobes are visible from one location in an open office. What must be confirmed during commissioning?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1031
- D: Their flashes are synchronized
Explanation
Where more than two visible appliances are in any field of view, they must flash in synchrony to reduce the risk of photosensitive seizures. Combined unsynchronized flash rates can exceed safe levels even if each strobe alone is within limits.