A strobe in a hotel guest room for a guest with hearing loss is mounted 30 in below the ceiling. What minimum intensity is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1032
- C: 110 cd minimum
Explanation
In sleeping areas a visible appliance mounted within 24 in of the ceiling needs at least 177 cd, while one mounted more than 24 in below the ceiling needs at least 110 cd. Smoke stratifies at the ceiling, so the higher position needs more intensity to wake a sleeper.