Question 1035 of 297 · NICET Fire Alarm Systems Level III
After a change to site-specific software that is not supposed to affect most of the system, which reacceptance testing is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1035
- D: Affected functions plus 10 percent of unaffected initiating devices, up to 50
Explanation
When site-specific software is changed, NFPA 72 requires testing all functions known to be affected and a sample of 10 percent of initiating devices not directly affected, up to a maximum of 50 devices. This verifies the change did not break unrelated programming.
More questions: Installation
- 1037How must the cabinet that holds the fire alarm record documents be identified?
- 1038How must a copy of the site-specific software be kept for a new system?
- 1039What is the typical format NFPA 72 suggests for presenting the sequence of operations in shop drawings and record documents?
- 1040When is the record of completion for a new fire alarm system prepared and provided?
- 1041During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?
- 1042What does the term as-built drawings, or record drawings, mean in the closeout package?