Question 1034 of 297 · NICET Fire Alarm Systems Level III
What portion of a new fire alarm system must be tested during initial acceptance testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1034
- A: 100 percent of all devices, appliances, and functions
Explanation
Initial acceptance testing covers every device, appliance, circuit, and function of the new system. Sampling is allowed only in specific reacceptance situations. The Level III should make sure the contractor pretest covers everything before the AHJ witness test.
More questions: Installation
- 1035After a change to site-specific software that is not supposed to affect most of the system, which reacceptance testing is required?
- 1037How must the cabinet that holds the fire alarm record documents be identified?
- 1038How must a copy of the site-specific software be kept for a new system?
- 1039What is the typical format NFPA 72 suggests for presenting the sequence of operations in shop drawings and record documents?
- 1040When is the record of completion for a new fire alarm system prepared and provided?
- 1041During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?