What signal characteristic must audible appliances in sleeping areas of a new hotel produce to wake occupants?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1033
- C: A low frequency signal with a 520 Hz fundamental
Explanation
Research showed that a 520 Hz square wave signal wakes people, including those with mild hearing loss or who are impaired, far better than high frequency tones. NFPA 72 therefore requires a low frequency signal in sleeping areas for audible appliances used to awaken occupants.