How must a copy of the site-specific software be kept for a new system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1038
- D: On-site, in nonvolatile, nonrewritable form
Explanation
NFPA 72 requires a copy of the site-specific software to be stored on-site in nonvolatile, nonerasable, nonrewritable memory, such as a write-once disc. This allows the program to be restored if the panel memory is lost or the contractor changes.
More questions: Installation
- 1039What is the typical format NFPA 72 suggests for presenting the sequence of operations in shop drawings and record documents?
- 1040When is the record of completion for a new fire alarm system prepared and provided?
- 1041During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?
- 1042What does the term as-built drawings, or record drawings, mean in the closeout package?
- 1043Before field devices are connected, your crew plans to test new cable runs with an insulation resistance tester. What is the main precaution?
- 1044Which of the following must be confirmed for two-wire smoke detectors connected to a conventional initiating device circuit?