Question 1041 of 297 · NICET Fire Alarm Systems Level III
During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1041
- D: Check the new locations against code, revise the drawings, and resubmit as required
Explanation
Field changes have to be checked against code and documented, and deviations from approved plans usually require resubmittal to the AHJ. The record drawings must reflect what is actually installed, so changes must be captured as they happen, not reconstructed at closeout.
More questions: Installation
- 1042What does the term as-built drawings, or record drawings, mean in the closeout package?
- 1043Before field devices are connected, your crew plans to test new cable runs with an insulation resistance tester. What is the main precaution?
- 1044Which of the following must be confirmed for two-wire smoke detectors connected to a conventional initiating device circuit?
- 1045Lead-acid batteries for the fire alarm system are delivered to the site. Which marking must the batteries carry?
- 1046A ceiling smoke detector on the drawings lands 2 ft from a supply air diffuser. What is the minimum distance you should direct the installer to maintain?
- 1047A spot smoke detector must be mounted on a sidewall because the ceiling is inaccessible. Where must it be placed?