When is the record of completion for a new fire alarm system prepared and provided?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1040
- C: After installation and acceptance testing, then kept with the record documents
Explanation
The record of completion documents what was installed and that it was tested and accepted. It is completed at the end of installation and acceptance testing and becomes part of the record documentation kept for the system.
More questions: Installation
- 1041During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?
- 1042What does the term as-built drawings, or record drawings, mean in the closeout package?
- 1043Before field devices are connected, your crew plans to test new cable runs with an insulation resistance tester. What is the main precaution?
- 1044Which of the following must be confirmed for two-wire smoke detectors connected to a conventional initiating device circuit?
- 1045Lead-acid batteries for the fire alarm system are delivered to the site. Which marking must the batteries carry?
- 1046A ceiling smoke detector on the drawings lands 2 ft from a supply air diffuser. What is the minimum distance you should direct the installer to maintain?