What is the typical format NFPA 72 suggests for presenting the sequence of operations in shop drawings and record documents?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1039
- A: An input/output matrix
Explanation
The sequence of operations shows which output each input initiates. NFPA 72 calls for it in the form of an input/output matrix or a narrative, and the matrix is the most common because it is easy to test against line by line during commissioning.
More questions: Installation
- 1040When is the record of completion for a new fire alarm system prepared and provided?
- 1041During a site visit you discover an electrician has relocated six smoke detectors to avoid new ductwork, and the approved shop drawings no longer match. What is the correct Level III response?
- 1042What does the term as-built drawings, or record drawings, mean in the closeout package?
- 1043Before field devices are connected, your crew plans to test new cable runs with an insulation resistance tester. What is the main precaution?
- 1044Which of the following must be confirmed for two-wire smoke detectors connected to a conventional initiating device circuit?
- 1045Lead-acid batteries for the fire alarm system are delivered to the site. Which marking must the batteries carry?