Question 1044 of 297 · NICET Fire Alarm Systems Level III
Which of the following must be confirmed for two-wire smoke detectors connected to a conventional initiating device circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1044
- C: They are listed as compatible with the specific control unit
Explanation
Two-wire smoke detectors draw power from the initiating circuit, so the control unit and detectors must be listed as compatible. An incompatible combination can fail to alarm or fail to reset even though both products are individually listed.
More questions: Installation
- 1045Lead-acid batteries for the fire alarm system are delivered to the site. Which marking must the batteries carry?
- 1046A ceiling smoke detector on the drawings lands 2 ft from a supply air diffuser. What is the minimum distance you should direct the installer to maintain?
- 1047A spot smoke detector must be mounted on a sidewall because the ceiling is inaccessible. Where must it be placed?
- 1048An installer mounts a spot heat detector on a wall. Which location complies with NFPA 72?
- 1049In a room with a peaked ceiling, where should the first row of spot smoke detectors be placed?
- 1050During pretest, a technician activates a detector in Room 214 and the annunciator shows Room 241. What is the correct fix before acceptance?