Question 1043 of 297 · NICET Fire Alarm Systems Level III
Before field devices are connected, your crew plans to test new cable runs with an insulation resistance tester. What is the main precaution?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1043
- B: Isolate all devices and the control unit so the test voltage cannot damage them
Explanation
Insulation resistance testers apply several hundred volts or more to find leakage and grounds. Fire alarm electronics in devices and the control unit can be damaged, so cable testing is done before connection, or with all equipment isolated.