During acceptance testing, how do you verify ground fault monitoring on each circuit?

Exactly one answer is correct.

Show solution

Correct answer to question 1054

  • C: Connect a ground to the circuit and confirm the trouble signal, then restore it

Explanation

Ground fault detection is tested by introducing a ground on each monitored circuit and confirming the control unit annunciates a trouble condition. Removing a device tests open circuit supervision, not ground fault detection.