Question 1054 of 297 · NICET Fire Alarm Systems Level III
During acceptance testing, how do you verify ground fault monitoring on each circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1054
- C: Connect a ground to the circuit and confirm the trouble signal, then restore it
Explanation
Ground fault detection is tested by introducing a ground on each monitored circuit and confirming the control unit annunciates a trouble condition. Removing a device tests open circuit supervision, not ground fault detection.