What secondary power duration does NFPA 72 require for a typical protected premises fire alarm system without voice evacuation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1056
- B: 24 hours of standby followed by 5 minutes of alarm
Explanation
The general requirement is 24 hours of quiescent load followed by 5 minutes of alarm with all notification appliances operating. Emergency voice/alarm communication systems need 15 minutes of alarm at maximum connected load instead of 5.