How long must the fire alarm record documentation (record drawings, record of completion, sequence of operation) be kept?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1060
- B: For the life of the system
Explanation
Record documentation describes the installed system and is needed for every future test, repair, and modification. NFPA 72 requires it to be maintained for the life of the system, which is longer than the retention period for individual inspection and test records.