For an in-building emergency voice/alarm communications system, how long must the secondary supply operate in alarm after 24 hours of standby?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1057
- C: 15 minutes at maximum connected load
Explanation
Voice systems may need to deliver messages over a longer period during staged or partial evacuation, so the alarm duration is 15 minutes at maximum connected load. The 5 minute duration applies to ordinary evacuation signaling.