Question 1055 of 297 · NICET Fire Alarm Systems Level III
During acceptance testing, primary power to the control unit is disconnected. What result shows correct operation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1055
- D: A trouble signal, transfer to batteries without loss of signals, and alarms still working
Explanation
Loss of primary power must produce a trouble signal and the system must keep operating on secondary power without losing any signals. Alarms are tested while on batteries to confirm the secondary supply can carry the load.
More questions: Installation
- 1056What secondary power duration does NFPA 72 require for a typical protected premises fire alarm system without voice evacuation?
- 1057For an in-building emergency voice/alarm communications system, how long must the secondary supply operate in alarm after 24 hours of standby?
- 1058Your project specifies a listed standby generator as part of the secondary supply. Under NFPA 72, what minimum battery capacity is still needed?
- 1059Which items does NFPA 72 list as part of the record documentation turned over to the owner at completion?
- 1060How long must the fire alarm record documentation (record drawings, record of completion, sequence of operation) be kept?
- 1061What qualification does NFPA 72 list as acceptable for persons who prepare fire alarm system plans and specifications?