Your project specifies a listed standby generator as part of the secondary supply. Under NFPA 72, what minimum battery capacity is still needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1058
- A: Enough to run the system for 4 hours
Explanation
Where an automatic starting generator meeting the code is used, NFPA 72 still requires storage batteries, but with capacity for 4 hours of operation instead of the full 24 hours. The batteries carry the system through generator start and transfer and any short outage.