Your project specifies a listed standby generator as part of the secondary supply. Under NFPA 72, what minimum battery capacity is still needed?

Exactly one answer is correct.

Show solution

Correct answer to question 1058

  • A: Enough to run the system for 4 hours

Explanation

Where an automatic starting generator meeting the code is used, NFPA 72 still requires storage batteries, but with capacity for 4 hours of operation instead of the full 24 hours. The batteries carry the system through generator start and transfer and any short outage.