A fire alarm interface relay will release the hold-open power for corridor smoke doors. How should the release be wired so it is fail-safe?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1082
- D: So that loss of power or an open wire to the holder releases the door
Explanation
Door holders are arranged so the door closes whenever power to the holder is interrupted, whether by the fire alarm relay, a power outage or a broken wire. That fail-safe arrangement keeps the smoke barrier intact under failure conditions.