Question 1081 of 297 · NICET Fire Alarm Systems Level III
During rough-in inspection on a new office building, you find several fire alarm junction boxes above a hard lid ceiling with no access panel. What is the main concern?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1081
- C: Boxes and connections must remain accessible for service and testing
Explanation
The NEC requires junction boxes to remain accessible without removing building finish. Splices hidden above an inaccessible ceiling cannot be serviced and will cause trouble later, so access panels or relocation are needed before the ceiling is finished.
More questions: Installation
- 1082A fire alarm interface relay will release the hold-open power for corridor smoke doors. How should the release be wired so it is fail-safe?
- 1083On a project where the AHJ requires a fire watch during the cutover from the old system to the new one, who is normally responsible for providing it?
- 1084A technician sets the panel to bypass the entire third floor while the ceiling contractor works there. Which control does the Level III need to ensure?
- 1085Which situation requires the installing contractor to perform reacceptance testing?
- 1086What is the purpose of the commissioning or acceptance test report signed at the end of the project?
- 1087A field change adds a new corridor with no manual boxes or notification on the approved plans. Which document change must the Level III make sure is completed?