Question 1087 of 297 · NICET Fire Alarm Systems Level III
A field change adds a new corridor with no manual boxes or notification on the approved plans. Which document change must the Level III make sure is completed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1087
- B: Revised shop drawings, calculations, and sequence of operations, submitted for approval
Explanation
Additions alter coverage, circuit loading, and battery capacity, so drawings and calculations must be revised and usually resubmitted. The record documents must reflect the final installation at closeout.
More questions: Installation
- 1088Which statement correctly describes the AHJ's role during the acceptance test?
- 1089Before the final acceptance test, who should receive training on operating the fire alarm system?
- 1090At the pre-acceptance inspection you find spot smoke detectors installed in the pockets between deep beams rather than on the bottom of the beams as shown on the approved drawings. What is the correct response?
- 1001A Level II technician proposes feeding a new fire alarm control unit from a GFCI protected receptacle circuit in the electrical room. What should the Level III project lead require instead?
- 1002During a site walk you find the breaker that serves the fire alarm control unit. Which condition must you verify for that circuit disconnecting means?
- 1003On a tenant improvement project the crew finds old fire alarm cable above an accessible ceiling that is no longer terminated at either end and is not tagged for future use. What does the NEC require?