Question 1085 of 297 · NICET Fire Alarm Systems Level III
Which situation requires the installing contractor to perform reacceptance testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1085
- D: After adding, removing, or modifying devices, wiring, or site-specific software
Explanation
Reacceptance testing is required whenever the system is altered: devices added or removed, wiring changed, control equipment replaced, or software modified. The scope depends on what changed, from the affected devices up to a sampled retest for software changes.
More questions: Installation
- 1086What is the purpose of the commissioning or acceptance test report signed at the end of the project?
- 1087A field change adds a new corridor with no manual boxes or notification on the approved plans. Which document change must the Level III make sure is completed?
- 1088Which statement correctly describes the AHJ's role during the acceptance test?
- 1089Before the final acceptance test, who should receive training on operating the fire alarm system?
- 1090At the pre-acceptance inspection you find spot smoke detectors installed in the pockets between deep beams rather than on the bottom of the beams as shown on the approved drawings. What is the correct response?
- 1001A Level II technician proposes feeding a new fire alarm control unit from a GFCI protected receptacle circuit in the electrical room. What should the Level III project lead require instead?