Question 1084 of 297 · NICET Fire Alarm Systems Level III
A technician sets the panel to bypass the entire third floor while the ceiling contractor works there. Which control does the Level III need to ensure?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1084
- B: The bypass is documented, notified, limited to what is needed, and removed when work ends
Explanation
Disabling part of a system is an impairment. It must be tracked, the right people notified, interim measures considered, and the bypass removed as soon as the cause is gone. Forgotten bypasses are a common cause of fire losses.
More questions: Installation
- 1085Which situation requires the installing contractor to perform reacceptance testing?
- 1086What is the purpose of the commissioning or acceptance test report signed at the end of the project?
- 1087A field change adds a new corridor with no manual boxes or notification on the approved plans. Which document change must the Level III make sure is completed?
- 1088Which statement correctly describes the AHJ's role during the acceptance test?
- 1089Before the final acceptance test, who should receive training on operating the fire alarm system?
- 1090At the pre-acceptance inspection you find spot smoke detectors installed in the pockets between deep beams rather than on the bottom of the beams as shown on the approved drawings. What is the correct response?