A technician sets the panel to bypass the entire third floor while the ceiling contractor works there. Which control does the Level III need to ensure?

Exactly one answer is correct.

Show solution

Correct answer to question 1084

  • B: The bypass is documented, notified, limited to what is needed, and removed when work ends

Explanation

Disabling part of a system is an impairment. It must be tracked, the right people notified, interim measures considered, and the bypass removed as soon as the cause is gone. Forgotten bypasses are a common cause of fire losses.