Question 1090 of 297 · NICET Fire Alarm Systems Level III

At the pre-acceptance inspection you find spot smoke detectors installed in the pockets between deep beams rather than on the bottom of the beams as shown on the approved drawings. What is the correct response?

Exactly one answer is correct.

Show solution

Correct answer to question 1090

  • D: Check the approved layout and code, then correct it or get a change approved

Explanation

Field conditions that differ from approved drawings must be checked against code and the design intent. Either correct the installation or process an approved revision so record drawings match the field.

Next to question ›