Question 1089 of 297 · NICET Fire Alarm Systems Level III
Before the final acceptance test, who should receive training on operating the fire alarm system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1089
- C: The owner's designated staff
Explanation
NFPA 72 expects the owner's personnel to be instructed in operating the system, including silencing, resetting, and recognizing signals. Training before handover reduces unwanted alarms and misuse.
More questions: Installation
- 1090At the pre-acceptance inspection you find spot smoke detectors installed in the pockets between deep beams rather than on the bottom of the beams as shown on the approved drawings. What is the correct response?
- 1001A Level II technician proposes feeding a new fire alarm control unit from a GFCI protected receptacle circuit in the electrical room. What should the Level III project lead require instead?
- 1002During a site walk you find the breaker that serves the fire alarm control unit. Which condition must you verify for that circuit disconnecting means?
- 1003On a tenant improvement project the crew finds old fire alarm cable above an accessible ceiling that is no longer terminated at either end and is not tagged for future use. What does the NEC require?
- 1004While inspecting rough-in, you see fire alarm cable laid directly on the lay-in ceiling tiles and tied to the ceiling grid wires. What is the correct direction to the installer?
- 1005Power-limited fire alarm cable must be run without raceway through a ceiling cavity that is used as a return air plenum. Which cable type is required?