A Level II technician proposes feeding a new fire alarm control unit from a GFCI protected receptacle circuit in the electrical room. What should the Level III project lead require instead?

Exactly one answer is correct.

Show solution

Correct answer to question 1001

  • A: A dedicated branch circuit not supplied through a GFCI or AFCI device

Explanation

Primary power for the fire alarm system must come from a dedicated branch circuit, and the NEC does not allow that branch circuit to be supplied through ground-fault or arc-fault circuit interrupters because a nuisance trip would silently drop the system to batteries. Cord and plug connections and shared lighting circuits do not meet the dedicated circuit rule.