On a tenant improvement project the crew finds old fire alarm cable above an accessible ceiling that is no longer terminated at either end and is not tagged for future use. What does the NEC require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1003
- D: Remove the accessible portion of the abandoned cable
Explanation
Article 760 treats cable that is not terminated at equipment and not identified for future use as abandoned, and the accessible portion must be removed. Abandoned cable adds fuel load and smoke in ceiling spaces, which is why simply cutting or taping it is not acceptable.
More questions: Installation
- 1004While inspecting rough-in, you see fire alarm cable laid directly on the lay-in ceiling tiles and tied to the ceiling grid wires. What is the correct direction to the installer?
- 1005Power-limited fire alarm cable must be run without raceway through a ceiling cavity that is used as a return air plenum. Which cable type is required?
- 1006An electrician wants to pull power-limited fire alarm conductors into the same conduit as 120 V lighting branch circuit conductors to save time. What is the correct ruling?
- 1007Your crew has run fire alarm cable through a 2-hour rated corridor wall. What must you confirm before the wall is closed up?
- 1008Which description matches pathway survivability Level 3 in NFPA 72?
- 1009On a Class A initiating device circuit, the specifications require the outgoing and return conductors to follow separate routes. Where does NFPA 72 permit them to run together in the same cable or raceway?