Question 1002 of 297 · NICET Fire Alarm Systems Level III
During a site walk you find the breaker that serves the fire alarm control unit. Which condition must you verify for that circuit disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1002
- C: It is marked red, labeled FIRE ALARM CIRCUIT, and accessible only to authorized personnel
Explanation
The code requires the disconnecting means for the fire alarm branch circuit to be marked red, identified as a fire alarm circuit, and protected against unauthorized operation. Its location must also be recorded at the control unit so service personnel can find it.
More questions: Installation
- 1003On a tenant improvement project the crew finds old fire alarm cable above an accessible ceiling that is no longer terminated at either end and is not tagged for future use. What does the NEC require?
- 1004While inspecting rough-in, you see fire alarm cable laid directly on the lay-in ceiling tiles and tied to the ceiling grid wires. What is the correct direction to the installer?
- 1005Power-limited fire alarm cable must be run without raceway through a ceiling cavity that is used as a return air plenum. Which cable type is required?
- 1006An electrician wants to pull power-limited fire alarm conductors into the same conduit as 120 V lighting branch circuit conductors to save time. What is the correct ruling?
- 1007Your crew has run fire alarm cable through a 2-hour rated corridor wall. What must you confirm before the wall is closed up?
- 1008Which description matches pathway survivability Level 3 in NFPA 72?