How is a nonrestorable line-type heat detector checked during periodic testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2008
- B: Without heat: function test plus loop resistance compared with the baseline
Explanation
Applying heat would destroy a nonrestorable line-type detector. Instead it is tested for function and its loop resistance is measured and compared with the value recorded at acceptance, which reveals damage or deterioration.