A notification appliance circuit is in trouble. With the field wiring disconnected from the panel, you measure the resistance across the two field conductors and read an open circuit instead of the end-of-line resistor value. What does this indicate?

Exactly one answer is correct.

Show solution

Correct answer to question 2036

  • A: An open somewhere in the field wiring or at a device

Explanation

With a healthy circuit, the meter should read approximately the end-of-line resistor value plus wire resistance. An infinite reading means the path to the resistor is broken, typically a loose terminal, broken wire, or failed connection at an appliance.