Question 2037 of 297 · NICET Fire Alarm Systems Level III
A short on a signaling line circuit drops out 120 devices on a large floor. Which design feature limits how many devices are lost to one short?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2037
- B: Short circuit isolation modules installed at intervals on the circuit
Explanation
Isolators open the circuit on either side of a short, so only the devices between two isolators are lost. NFPA 72 and the manufacturer set limits on how many devices may be lost to a single fault, which drives isolator placement.
More questions: Maintenance
- 2038During the annual inspection of a 24 VDC system, you measure 27.3 V across the battery terminals with the charger connected. What does this reading usually indicate?
- 2039During the annual test of a duct smoke detector, which check is needed besides the functional alarm test?
- 2040During annual testing of an air-sampling smoke detection system, what transport time requirement applies to the farthest sampling port?
- 2041An addressable smoke detector reports a maintenance alert because its drift compensation has reached its limit. What is the correct response?
- 2042Which personnel does NFPA 72 recognize as qualified to perform inspection, testing, and maintenance of fire alarm systems?
- 2043Before the annual visit at a central station monitored building, what should the technician confirm with the central station operator?