Question 2037 of 297 · NICET Fire Alarm Systems Level III

A short on a signaling line circuit drops out 120 devices on a large floor. Which design feature limits how many devices are lost to one short?

Exactly one answer is correct.

Show solution

Correct answer to question 2037

  • B: Short circuit isolation modules installed at intervals on the circuit

Explanation

Isolators open the circuit on either side of a short, so only the devices between two isolators are lost. NFPA 72 and the manufacturer set limits on how many devices may be lost to a single fault, which drives isolator placement.

Next to question ›