A central station receives a supervisory signal for a closed sprinkler valve. What action does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2051
- D: Notify designated personnel promptly and dispatch a runner if required
Explanation
Supervisory signals indicate an off-normal condition of a protection system and must be communicated promptly to the designated personnel, with a runner or maintenance person dispatched where required. They are not handled as fire alarms.
More questions: Maintenance
- 2052A new account uses a digital alarm communicator transmitter. Which arrangement meets NFPA 72?
- 2053A building's fire alarm communicator was converted to an IP path with cellular backup. What must be verified during the annual test?
- 2054A site has 300 fixed-temperature nonrestorable spot heat detectors that reached 15 years of service. If the owner chooses sampling rather than replacement, how many must be sent for laboratory testing?
- 2055A site-specific software change affects only the elevator recall programming. The system has 620 initiating devices not affected by the change. How many of them must be tested during reacceptance?
- 2056A software change affects one floor of a system with 300 initiating devices not affected by the change. How many unaffected initiating devices must be tested?
- 2057Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?