Question 2053 of 297 · NICET Fire Alarm Systems Level III
A building's fire alarm communicator was converted to an IP path with cellular backup. What must be verified during the annual test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2053
- A: That each communication path works and its failure is reported as trouble
Explanation
With multiple paths, each path must be tested and a failure of any path must be annunciated at the premises and the supervising station within the times NFPA 72 specifies. Testing only one path can leave a silent failure on the other.
More questions: Maintenance
- 2054A site has 300 fixed-temperature nonrestorable spot heat detectors that reached 15 years of service. If the owner chooses sampling rather than replacement, how many must be sent for laboratory testing?
- 2055A site-specific software change affects only the elevator recall programming. The system has 620 initiating devices not affected by the change. How many of them must be tested during reacceptance?
- 2056A software change affects one floor of a system with 300 initiating devices not affected by the change. How many unaffected initiating devices must be tested?
- 2057Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?
- 2058A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?
- 2059During the annual inspection you find that a painter has painted several smoke detectors along with the ceiling. What should you do?