Question 2052 of 297 · NICET Fire Alarm Systems Level III
A new account uses a digital alarm communicator transmitter. Which arrangement meets NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2052
- B: Two separate means of transmission, one of which may be a telephone line
Explanation
A DACT must be connected to two separate means of transmission, so a single phone line failure does not cut off signals. The second path can be another telephone line, a cellular path, or another approved method.
More questions: Maintenance
- 2053A building's fire alarm communicator was converted to an IP path with cellular backup. What must be verified during the annual test?
- 2054A site has 300 fixed-temperature nonrestorable spot heat detectors that reached 15 years of service. If the owner chooses sampling rather than replacement, how many must be sent for laboratory testing?
- 2055A site-specific software change affects only the elevator recall programming. The system has 620 initiating devices not affected by the change. How many of them must be tested during reacceptance?
- 2056A software change affects one floor of a system with 300 initiating devices not affected by the change. How many unaffected initiating devices must be tested?
- 2057Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?
- 2058A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?