Question 2056 of 297 · NICET Fire Alarm Systems Level III
A software change affects one floor of a system with 300 initiating devices not affected by the change. How many unaffected initiating devices must be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2056
- B: 30
Explanation
Ten percent of 300 unaffected devices is 30, which is below the 50 device cap, so 30 devices are tested in addition to everything on the affected floor.
More questions: Maintenance
- 2057Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?
- 2058A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?
- 2059During the annual inspection you find that a painter has painted several smoke detectors along with the ceiling. What should you do?
- 2060Months after a renovation, your technician finds plastic dust covers still on several smoke detectors. How should this be handled?
- 2061A tenant has placed a large storage cabinet in front of a manual fire alarm box. What is the proper handling?
- 2062A new tenant hung a large banner that blocks the view of a strobe in an open area. What should the inspection report say?