Question 2055 of 297 · NICET Fire Alarm Systems Level III

A site-specific software change affects only the elevator recall programming. The system has 620 initiating devices not affected by the change. How many of them must be tested during reacceptance?

Exactly one answer is correct.

Show solution

Correct answer to question 2055

  • C: 50

Explanation

The rule is 10 percent of initiating devices not directly affected, up to a maximum of 50. Ten percent of 620 is 62, which exceeds the cap, so 50 devices are tested, in addition to all functions known to be affected.