Question 2055 of 297 · NICET Fire Alarm Systems Level III
A site-specific software change affects only the elevator recall programming. The system has 620 initiating devices not affected by the change. How many of them must be tested during reacceptance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2055
- C: 50
Explanation
The rule is 10 percent of initiating devices not directly affected, up to a maximum of 50. Ten percent of 620 is 62, which exceeds the cap, so 50 devices are tested, in addition to all functions known to be affected.
More questions: Maintenance
- 2056A software change affects one floor of a system with 300 initiating devices not affected by the change. How many unaffected initiating devices must be tested?
- 2057Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?
- 2058A technician leaves the panel in walk test mode at the end of the day. Why is this a serious problem?
- 2059During the annual inspection you find that a painter has painted several smoke detectors along with the ceiling. What should you do?
- 2060Months after a renovation, your technician finds plastic dust covers still on several smoke detectors. How should this be handled?
- 2061A tenant has placed a large storage cabinet in front of a manual fire alarm box. What is the proper handling?