A 24 VDC notification circuit has 10 strobes drawing a total of 1.5 A. The farthest strobe is 300 ft from the panel on 14 AWG solid wire with 3.07 ohms per 1,000 ft. What is the approximate voltage drop at the end?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3005
- D: About 2.8 V
Explanation
Loop resistance: 2 x 300 ft = 600 ft, 600 / 1000 x 3.07 = 1.842 ohms. Drop: 1.5 A x 1.842 ohms = 2.76 V. This lumped-load method is conservative, because it assumes all current flows to the end of the circuit.
More questions: Submittal Preparation and System Layout
- 3006A strobe circuit is designed to start at a worst-case panel source voltage of 20.4 V. The strobes are listed for 16 to 33 V. What is the maximum allowable voltage drop on the circuit?
- 3007A 12 AWG stranded circuit has a resistance of 1.98 ohms per 1,000 ft. The load is 2.0 A at the end of a 250 ft run. What is the voltage drop?
- 3008A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?
- 3009What is the listed spacing of spot-type heat detectors in a room with a smooth ceiling 9 ft high, if the detector is listed for 50 ft?
- 3010A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?
- 3011A heat detector listed for 30 ft spacing is installed on a smooth ceiling 21 ft high. The multiplier for over 20 up to 22 ft is 0.58. What is the adjusted spacing?