Question 3006 of 297 · NICET Fire Alarm Systems Level III
A strobe circuit is designed to start at a worst-case panel source voltage of 20.4 V. The strobes are listed for 16 to 33 V. What is the maximum allowable voltage drop on the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3006
- A: 4.4 V
Explanation
The question states the worst-case source voltage of 20.4 V (roughly 85 percent of 24 V, a common design value for a battery near depletion). 20.4 V minus the 16 V minimum operating voltage gives 4.4 V allowable drop.
More questions: Submittal Preparation and System Layout
- 3007A 12 AWG stranded circuit has a resistance of 1.98 ohms per 1,000 ft. The load is 2.0 A at the end of a 250 ft run. What is the voltage drop?
- 3008A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?
- 3009What is the listed spacing of spot-type heat detectors in a room with a smooth ceiling 9 ft high, if the detector is listed for 50 ft?
- 3010A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?
- 3011A heat detector listed for 30 ft spacing is installed on a smooth ceiling 21 ft high. The multiplier for over 20 up to 22 ft is 0.58. What is the adjusted spacing?
- 3012Under the 0.7 rule, how far may a spot-type detector with a nominal 30 ft spacing be from any point on the ceiling?