Question 3004 of 297 · NICET Fire Alarm Systems Level III
In a battery calculation, which current values should be used for each device?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3004
- B: The manufacturer's published standby and alarm currents for each device
Explanation
Battery and power supply calculations use the published current draw from each product's data sheet, totaled by circuit and by power supply. Ignoring standby current is a common error, since 24 hours of standby usually dominates the result.
More questions: Submittal Preparation and System Layout
- 3005A 24 VDC notification circuit has 10 strobes drawing a total of 1.5 A. The farthest strobe is 300 ft from the panel on 14 AWG solid wire with 3.07 ohms per 1,000 ft. What is the approximate voltage drop at the end?
- 3006A strobe circuit is designed to start at a worst-case panel source voltage of 20.4 V. The strobes are listed for 16 to 33 V. What is the maximum allowable voltage drop on the circuit?
- 3007A 12 AWG stranded circuit has a resistance of 1.98 ohms per 1,000 ft. The load is 2.0 A at the end of a 250 ft run. What is the voltage drop?
- 3008A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?
- 3009What is the listed spacing of spot-type heat detectors in a room with a smooth ceiling 9 ft high, if the detector is listed for 50 ft?
- 3010A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?