A warehouse ceiling has beams 24 in deep and 10 ft on center. How should heat detection be laid out?

Exactly one answer is correct.

Show solution

Correct answer to question 3017

  • B: Treat each bay as a separate area needing detection

Explanation

When beams are deeper than 18 in and spaced more than 8 ft on center, each bay is a separate area, and detectors are laid out in each bay. Shallower beams use the two-thirds reduction instead.