A warehouse ceiling has beams 24 in deep and 10 ft on center. How should heat detection be laid out?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3017
- B: Treat each bay as a separate area needing detection
Explanation
When beams are deeper than 18 in and spaced more than 8 ft on center, each bay is a separate area, and detectors are laid out in each bay. Shallower beams use the two-thirds reduction instead.