Question 3018 of 297 · NICET Fire Alarm Systems Level III
A sloped ceiling rises 2 ft over a horizontal run of 10 ft. Is it a sloping ceiling under NFPA 72 detector placement rules?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3018
- D: Yes, because the slope exceeds 1 in 8
Explanation
A sloping ceiling has a slope greater than 1 in 8. Here 2 / 10 = 1 in 5, which is steeper, so the sloped ceiling rules apply, including a row of detectors within 3 ft of the peak measured horizontally.