For a peaked ceiling, where must the first row of spot detectors be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3019
- A: Within 36 in of the peak, measured horizontally
Explanation
On peaked ceilings, a detector row is located within 36 in horizontally of the peak. Additional detectors are laid out using the horizontal projection of the ceiling.