A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3045
- C: Yes, 5.7 A is under 6 A, but spare is thin
Explanation
Total alarm load: 1.4 + 1.6 + 1.2 + 1.5 = 5.7 A, which is under the 6 A rating. The margin is small, so many designers would add a supply or plan for spare capacity, and the battery calculation must also be checked.