A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?

Exactly one answer is correct.

Show solution

Correct answer to question 3045

  • C: Yes, 5.7 A is under 6 A, but spare is thin

Explanation

Total alarm load: 1.4 + 1.6 + 1.2 + 1.5 = 5.7 A, which is under the 6 A rating. The margin is small, so many designers would add a supply or plan for spare capacity, and the battery calculation must also be checked.