A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3044
- D: 45.6 W
Explanation
Connected load: 22 x 1 W + 8 x 2 W = 22 + 16 = 38 W. With 20 percent spare: 38 x 1.2 = 45.6 W, so a 50 W amplifier or larger would be selected.